→ circuit-breaker
a mechanical switching device, capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time and breaking currents under specified abnormal circuit conditions such as those of short-circuit.
a mechanical switching device, capable of making, carrying and breaking currents under normal circuit conditions and also making, carrying for a specified time and breaking currents under specified abnormal circuit conditions such as those of short-circuit.
← يعني ده جهاز فصل ميكانيكي قادر يفصل الدائرة الكهربية في الحالة العادية وفي حالة الظروف غير العادية زي الفصل علي ال Short Circuit .
→ Frame size
a term designating a group of circuit-breakers, the external physical dimensions of which are common to a range of current ratings.
→ Frame size
a term designating a group of circuit-breakers, the external physical dimensions of which are common to a range of current ratings.
و دى من الآخر المخ الخاص بالقاطع .
■ وراح كاتب لحضرتك Note جميله قالك ان ال Frame Size بيتسمي باسم أكبر تيار في المجموعة .
■ فعلي سبيل المثال لما أقول قاطع 40 و 63 و 80 و 100 أمبير .. وعاوز أقول ان هم التلاته لهم نفس الأبعاد هكتبهم ازاي ؟
■ وراح كاتب لحضرتك Note جميله قالك ان ال Frame Size بيتسمي باسم أكبر تيار في المجموعة .
■ فعلي سبيل المثال لما أقول قاطع 40 و 63 و 80 و 100 أمبير .. وعاوز أقول ان هم التلاته لهم نفس الأبعاد هكتبهم ازاي ؟
← 40/100 >> والقاطع ده أقصي قيمة تيار ممكن أخدها منه هي 40 أمبير .. لأن قيمة ال Trip unit هنا أقصي قيمه لها هي 40 أمبير .. اومال ايه ال 100 ؟ .. زى ما اتفقنا حاجه بتعبر ان اي حاجه number / 100 هيكون لها نفس الأبعاد .
← 63/100 >> قاطع أقصي حاجه أقدر أخدها منه هي 63 أمبير ..
← 63/100 >> قاطع أقصي حاجه أقدر أخدها منه هي 63 أمبير ..
طب ينفع أخد منه 40 أمبير ؟ .. ان ممكن تظبط ال trip unit نفسها علي قيمه من أول 0.4 الي 1 .
← 100/100 .. أقصي تيار أقدر اخده منه هو 100 أمبير .. وممكن أخد منه ال 63 وال 40 عن طريق ضبط ال trip unit علي نسبه من أقصي تيار لها .
← 100/100 .. أقصي تيار أقدر اخده منه هو 100 أمبير .. وممكن أخد منه ال 63 وال 40 عن طريق ضبط ال trip unit علي نسبه من أقصي تيار لها .
Nominal current ( In) is the max current a breaker could make, carry and break during normal operation conditions
Regulated Current ( Ir ) Long time pick up Current setting ( or thermal setting ) . This is multiplication coefficient of the rating of the device (Ir = x In )
Regulated Current ( Ir ) Long time pick up Current setting ( or thermal setting ) . This is multiplication coefficient of the rating of the device (Ir = x In )
• In >> is the rated current of the protective device; for adjustable protective releases, the rated current In is the set current;
■ فا حضرتك كاستشاري المفروض لا تكتب Frame Size علي ال Single Line diagram بتاعك ولا في Panel Schedule .. حضرتك اكتب ال Set Current
■ فا حضرتك كاستشاري المفروض لا تكتب Frame Size علي ال Single Line diagram بتاعك ولا في Panel Schedule .. حضرتك اكتب ال Set Current
اللى محتاج القاطع يفصل عنده وصمم الكابل عليه وسيب الباقي علي ال Supplier بتاع اللوحات .
■ ده Simulator عملاه ABB علي الموقع بتاعهم افتحه كده ومشي ايدك علي موضوع ال Trip units ده واعرف عنهم أكتر .
[new.abb.com](new.abb.com)
■ ده Simulator عملاه ABB علي الموقع بتاعهم افتحه كده ومشي ايدك علي موضوع ال Trip units ده واعرف عنهم أكتر .
[new.abb.com](new.abb.com)
او اكتب في جوجل
ABB trip unit simulator
حمل الصفحة اللي تهمنا من ال IEC Standard من هنا :
drive.google.com...
شكرا لحضراتكم اذا وصلت لنهاية التغريدة
والشكر موصول للمهندس / احمد مجدي
ABB trip unit simulator
حمل الصفحة اللي تهمنا من ال IEC Standard من هنا :
drive.google.com...
شكرا لحضراتكم اذا وصلت لنهاية التغريدة
والشكر موصول للمهندس / احمد مجدي